What is a power transformer?
Products in the power transformers family include those designed for transformation of AC utility power at nominal frequencies of 400 Hz or less that contain galvanically isolated primary and secondary windings. They are not packaged or equipped with the common connectors used for AC utility powered products, making them unserviceable as an end-use product in an isolation transformer capacity.
Introduction to DigiKey’s Product Selection Guide
This page is one of many in DigiKey’s Product Selection Guide (PSG). This particular page is focused on power transformers. It provides a description of the individual parameters used to characterize the part. This information will allow you to better understand and navigate DigiKey’s parametric search engine. Click here for a case study showing how to use the search tools.
How are power transformers categorized?
-
Type: Refers to the specific construction or design configuration of the transformer’s core and winding arrangement.
-
Voltage - Primary: Indicates nominal AC input voltages with which a device is designed for use: multiple values indicate different connection options, allowing production of the listed secondary voltages from any of the listed primary voltages.
-
Voltage - Secondary (Full Load): Nominal AC RMS output voltage appearing at the device output windings when the rated output current is being drawn and the nominal primary voltage is applied.
-
Current - Output (Max): The maximum amount of current that can be output by the device.
-
Primary Winding(s): Describes the configuration of the transformer’s primary winding(s), which are those typically connected to a power source.
-
Secondary Winding(s): Indicates the number of separate windings present on the side of the transformer that is typically used to deliver power to a load.
-
Center Tap: Indicates whether or not a user-accessible connection to the midpoint of the secondary winding is present.
-
Power - Max: Typically this represents the maximum power rating to which a device will meet its given specifications. Exceeding this power rating may damage the device and other system components.
-
Mounting Type: Indicates how the device is attached.
-
Termination Style: Selection of termination style used to connect the device to a system, such as PC pin, solder pad, or wire leads.
-
Size / Dimension: The physical dimensions of the device, typically listed in length and width or diameter.
-
Height - Seated (Max): Indicates how far the device will extend above the surface to which it has been attached.
-
Voltage - Isolation: Indicates the level of electrical isolation provided between the primary and secondary windings of the transformer.
-
Weight: Indicates the overall weight of the transformer, typically listed in pounds or grams.
Examples of power transformers
Schematic symbol
The schematic symbol for a transformer is shown below.
Schematic symbols courtesy of Scheme-it.
Related media links
Videos
- VPT Series of Toroidal Power Transformers
- WEbinar Powered by DigiKey: Basics of Power
DigiKey Tech Forum articles
- An Engineer’s Perspective on Power Transformers
- Power Transformer - inherently and non-inherently limited - Power / Transformers
- Transformers vs. Power Supplies
- Transformer Rated Power Capacity
- Triad Magnetics Transformers “B” Suffix
- Transformer Primary / Secondary Impedance
Follow up
If you have any general questions on the specifications for selecting power transformers, please reply using the button below. If you have questions on a specific transformer, please post your questions in the forum’s transformers category.
Transformer Ultimate Guide - Meta Power Solutions
Turns ratio is generally represented by the letter “a”.
a > 1 (NP>NS): the transformer is a step-down transformer
a < 1 (NP
a = 1 (NP=NS): 1-to-1 (Isolation) transformer has equal input and output voltages
The turns ratio of a transformer is important because it determines the ratio of primary voltage to secondary voltage. By formula,
Goto Tianya to know more.
For the transformer above, this formula indicates that the voltage across the primary is four times the voltage across the secondary.
IMPORTANT!
Power on the primary and secondary sides of the transformer always remains the same. KVA on the Primary Side = KVA on the secondary Side (Under Ideal Conditions, Ignoring Losses) KVA on the Primary Side = 1.732 × Voltage across Primary × Current through Primary KVA on the Secondary Side = 1.732 × Voltage across Secondary × Current through Secondary
According to Section 450.11 of the NEC, each transformer must have a nameplate indicating the following:
- Name of the transformer manufacturer
- Transformer KVA rating
- Frequency
- Primary and Secondary Voltages
- Transformer Impedance (25 KVA and higher only)
- Amount and kind of insulating liquid (liquid-type transformer)
- Insulation temperature class (dry-type transformer)
Tap Changer
Taps on the primary winding compensate for variations in line voltage. Tap increments are usually 2.5 % or 5 %, both above or below the rated line voltage.
A transformer that is used to step down the voltages transmitted by power utilities to values that the customers require.
Distribution transformers are classified as being either Dry-Type or Wet-Type. These classifications indicate the means used to cool and/or insulate the components.
Dry-type transformers are generally air-cooled and may have louvres to aid in cooling.
Wet-type transformers are high-power transformers that generate too much heat and are typically cooled using mineral oil or high-temperature hydrocarbons.
EXAMPLE:
A 13,000Y/ to 208Y/120 transformer would have the following characteristics:
- The primary is Y-connected to a 13,000 V line voltage or a phase voltage of V.
- The secondary is Y-connected with a line voltage of 208V and a phase voltage of 120V.
- This is a Step-Down transformer.
ANSI standards require that the leads connected to high-voltage windings be marked with an H and leads connected to the low-voltage windings be marked with an X. If the transformer steps up the voltage, the primary winding (the winding to which voltage is applied) is the low-voltage, or X, winding. If the transformer steps down the voltage, the primary winding (the winding to which voltage is applied) is the high-voltage, or H, winding.
KVA is determined by the connected load of your equipment. The primary and the secondary KVA are exactly the same.
AS AN EXAMPLE:
Primary-Side: 100A @ 120V = 12,000VA or 12KVA [same as] Secondary-Side: 50A @ 240V = 12,000VA or 12KVA.
The following information is required to size any transformer:
- Is the system Single or Three-Phase?
- What is the frequency (Hz)?
- What is the voltage (line to line) of the “supply power” (i.e., primary)?
- What voltage is necessary for the load equipment (i.e., secondary)?
- What is the total load (in amperes) of your connected equipment (on the secondary side)?
With the above information, the transformer KVA can be calculated as:
Single-Phase Calculations:
Example:
Three-Phase Calculations:
Example:
After calculating the KVA rating, choose a Standard size transformer that is no less than the KVA needed.
IMPORTANT!
The Volts and Amps above can be either the Primary values OR the Secondary values, but NOT both. The KVA is the same on the Primary side and the Secondary side. The “Volts” are the Line to Line, NOT the Line to Neutral.